Tesla charger

Status
Not open for further replies.

nickelec

Senior Member
Location
US
Customer wants me to install Tesla charger she sent me the paperwork and it says Max 32 amp breaker what are you guys doing running number tens with 30-35 breaker or number 8 with a 40

Sent from my SM-G950U using Tapatalk
 
If it says max breaker, then you need 30a on #10; if that's the full current, then 40a on #8.

It's usually the latter in my experience with car chargers.
 
Ya i jsur left there it's max current so #8 on 40a breaker is where I'm going

Sent from my SM-G950U using Tapatalk
 
Out of curiosity, is this a NEMA receptacle installation, Tesla Wall Connector, or something else?
 
Last edited:
I think you are misreading something. The Tesla standard mobile charger, that comes with the car has a max 32 amp OUTPUT. It plugs into a NEMA 14-50 receptacle connected to a 50 amp breaker. You need to size everything at 50 amps.

All the optional Tesla charger adapters match up with standard NEMA receptacles and branch circuits sizes.

Edited to add link:
https://shop.tesla.com/us/en/product/vehicle-accessories/model-s_x_3-gen-2-nema-adapters?tesref=true

Read the first *note under the table.
 
I think you are misreading something. The Tesla standard mobile charger, that comes with the car has a max 32 amp OUTPUT. It plugs into a NEMA 14-50 receptacle connected to a 50 amp breaker. You need to size everything at 50 amps.

All the optional Tesla charger adapters match up with standard NEMA receptacles and branch circuits sizes.

Edited to add link:
https://shop.tesla.com/us/en/product/vehicle-accessories/model-s_x_3-gen-2-nema-adapters?tesref=true

Read the first *note under the table.
Seems that 40 amps should be acceptable.
 
Status