Tesla Universal Wall Connector - Wires Fanning Out Under Terminal Screw - Safe?

Location
United States
Occupation
N/A
The Gen 2 Tesla Wall Connector specifically stated that ferrules were safe to use. The new Gen 3 doesn’t mention anything about ferrules, so I assume they’re not approved.

When installing #8 THHN on a 50A Breaker (40A Charge rate) I notice the wires will NOT land perfectly flush under the terminal screw.

No matter how much they’re twisted and centered, the wires start to fan out when torquing to the required spec.


They’ve been torqued to spec, pulled on, and torqued to speed again. Will this cause any issues?
 
Location
United States
Occupation
N/A
No. You're using the terminal as designed and it is installed according to its instructions so you're good to go.

Welcome to the Forum. :)
I didn’t realize I had a typo, I meant “They’ve been torqued to spec, pulled on, and torqued to spec again.”

Glad to hear there aren’t any issues with the wire slightly fanning away from the screw and that this looks good and installed to spec! Thanks for having me in the forum (y)
 
Location
United States
Occupation
N/A
No. You're using the terminal as designed and it is installed according to its instructions so you're good to go.

Welcome to the Forum. :)
One more question…

Here’s a close up of L1 - You can see that this one wire fans out, but landed under the terminal screw.


If that wire ever touches the black plastic next to it (while still secured under the terminal screw) could that cause any issues like melting or heat build up?

I’m 99% sure it wouldn’t cause any issues, but wanted to ask. Thanks again!
 

retirede

Senior Member
Location
Illinois
A little aside but related to your concern. I am not pleased with many/most set screw terminals and often see strands not clamped well and even just floating in mid air. I am skeptical much actual testing is done with these things. In general I think a clamp type of termination would be better and wish that was the standard.

Agreed. Set screw terminals without a non-rotating clamping surface should be limited to solid wire.
 
Location
United States
Occupation
N/A
A little aside but related to your concern. I am not pleased with many/most set screw terminals and often see strands not clamped well and even just floating in mid air. I am skeptical much actual testing is done with these things. In general I think a clamp type of termination would be better and wish that was the standard.
Agreed. Set screw terminals without a non-rotating clamping surface should be limited to solid wire.
Agreed. A clamp type termination would be best!

I had one more question if you wouldn’t mind taking a look and providing feedback when you have a moment. Thanks
 

winnie

Senior Member
Location
Springfield, MA, USA
Occupation
Electric motor research
A little aside but related to your concern. I am not pleased with many/most set screw terminals and often see strands not clamped well and even just floating in mid air. I am skeptical much actual testing is done with these things. In general I think a clamp type of termination would be better and wish that was the standard.
It appears that the set screws twist right against the wires with no sort of saddle or intermediate protector.

IMHO these sort of connectors should always require (or at least permit) the use of ferrules.

I wonder if twisting the wires in the opposite direction would make them tighten up when the set screw twists against them.
 

MD Automation

Senior Member
Location
Maryland
Occupation
Engineer
In general I think a clamp type of termination would be better and wish that was the standard.
It appears that the set screws twist right against the wires with no sort of saddle or intermediate protector.
Agreed, a saddle type clamp where the screw does not bear directly on the wire is a much better connection, particularly for stranded wires.

This is a view of the redesigned Leviton 14-50R, showing exactly that type of connection. The Allen screw brings up the lower saddle to squeeze the entire wire - solid or stranded - against the fixed top plate.

IMG_3203.jpg
 
It appears that the set screws twist right against the wires with no sort of saddle or intermediate protector.

IMHO these sort of connectors should always require (or at least permit) the use of ferrules.

I wonder if twisting the wires in the opposite direction would make them tighten up when the set screw twists against them.
Yeah what is with ferrules anyway? They don't really seem to be a thing here in the states like they are in the rest of the world.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
The Gen 2 Tesla Wall Connector specifically stated that ferrules were safe to use. The new Gen 3 doesn’t mention anything about ferrules, so I assume they’re not approved.

When installing #8 THHN on a 50A Breaker (40A Charge rate) I notice the wires will NOT land perfectly flush under the terminal screw.

No matter how much they’re twisted and centered, the wires start to fan out when torquing to the required spec.


They’ve been torqued to spec, pulled on, and torqued to speed again. Will this cause any issues?
So assuming you made this termination what did your supervisor say? The members here are only viewing pictures, your supervisor is on site and would undoubtedly be able to critique better than we can.
 