We install a lot of Tesla wall connectors and other chargers. And recently we started installing them with Neurio active management controller which adjusts Wall Connector output to keep the panel load under 80%.
I feel like inspectors are a bit afraid of something that they haven't seen before and I just got a correction for 2 things:
1. Provide load calculation for the panel (which obviously will show overload without the device).
2. He said that we can't use the main panel as a j-box.. That's something new to me.. We installed a sub panel to free up some spaces and extend the wires to move few of the breakers there.. He said that we can't have wire nuts/extensions in the main panel..
I would really apreciate an advice to how I should approach this inspector.. We usually installed DCC shedders, but those are a bit more expensive and turn off chargers completely which is not ideal in some scenarios.
Thank you so much guys!
We install a lot of Tesla wall connectors and other chargers. And recently we started installing them with Neurio active management controller which adjusts Wall Connector output to keep the panel load under 80%.
I feel like inspectors are a bit afraid of something that they haven't seen before and I just got a correction for 2 things:
1. Provide load calculation for the panel (which obviously will show overload without the device).
2. He said that we can't use the main panel as a j-box.. That's something new to me.. We installed a sub panel to free up some spaces and extend the wires to move few of the breakers there.. He said that we can't have wire nuts/extensions in the main panel..
I would really apreciate an advice to how I should approach this inspector.. We usually installed DCC shedders, but those are a bit more expensive and turn off chargers completely which is not ideal in some scenarios.