what would i use to vertfy the output of high voltage lighting transformers between 10,000 and 20,000 volts?
what would i use to vertfy the output of high voltage lighting transformers between 10,000 and 20,000 volts?
thanks but its a little large to carry up a step ladder
Pull an arc with a screwdriver. If you get to at least 3/4", you're good.what would i use to vertfy the output of high voltage lighting transformers between 10,000 and 20,000 volts?
The "real" way is with a high voltage probe for your DMM. Some of the probes have a switch on the side for the range. In practice, I've had pretty good luck with pulling an arc with a screwdriver. Assuming the transformer was sized right in the first place, it's either dead or it works.
You should publish a book with all your esoteric troubleshooting knowledge. There's your million dollar idea.
Or maybe write a column for a trade magazine.![]()
For that sort of voltage, I have a couple of 40kV 'scope probes.what would i use to vertfy the output of high voltage lighting transformers between 10,000 and 20,000 volts?