good day all,
these motors and controls are killing me. I missed this question and have been working it over but can't get to the correct answer.
A 230-volt, 1 ½ horsepower single-phase AC motor is connected to a branch circuit supplied by #14 THW conductors. What is the MAXIMUM inverse time delay breaker permitted to protect this circuit?
1)40amp (correct answer)
2)30amp
3)25amp
4)20amp
ok so table 430.248 gives me 10amps
table 430.52(C)(1) tells me 250% 10*250%=25
or do you go 10*125% (for continuous duty which isn't mentioned in the question) =12.5 then 12.5*250%=31.25 which even if I round up is only a 35-amp breaker.
I have read through 430.52, they mention inverse time breakers in 430.52(c)(1)(b)(3) but I don't think that would pertain to this question.
where am I screwing this up??????
thanks very much