Test Q. A 240v single phase feeder with 2.0 alum thwn supplying an existing panel 260' from DP. whats max load that can be placed on the panel so that the VD is limited to 3%?
I = 133100x 7.2/2x21.2x260 = 86.9 0r 87a
a 2/0 alu thwn is good for 135a and the max load for 3% VD is 87a on feeder panel does that sound right?
I = 133100x 7.2/2x21.2x260 = 86.9 0r 87a
a 2/0 alu thwn is good for 135a and the max load for 3% VD is 87a on feeder panel does that sound right?