On the Master test I took this morning a factory calculation was asking about the wire size for a 50KW 208 volt 3 phase heater. Am I correct with the following calcuation:
50,000 divided by 360 (208 x 1.73) = 138.88
138.88 x 125% = 173.6
there for use 2/0 copper which is rated for 175 a
I referenced code art. 424.3 (B) 310.16
I ask because this answer was not on the answer sheet. I ran this calc. 3 times during the test plus talked with others after the test and they are coming up with the same thing.
I couldn't ask the test proctors due to they have no electrical knowledge. This causes 2 answer to be incorrect on the test. Taking a 5 point question to a 3 point. I am going to call the electrical board who gives the test on Monday ,but I wanted to check with some others first.
Either way I feel quite good about the test overall , but until I recieve the letter in the mail there will always be that question.