What size conductor is required for a 40 amp baseboard heater supplied with 240 volts?
I say that a #6 is required. The calculated load is 50 amps. I believe that you must use the 60 degree table for your conductors, which would put you at a # 6 wire.
See the book states #8 conductors is the correct answer. We know there have been errors in Stallcup's books before.
I say that a #6 is required. The calculated load is 50 amps. I believe that you must use the 60 degree table for your conductors, which would put you at a # 6 wire.
See the book states #8 conductors is the correct answer. We know there have been errors in Stallcup's books before.