equipment grounding conductors must be the same size as the circuit conductors for 15,20,30amps circuits. where in the nec can i fined this? :confused:
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
Re: test time

Well to be acurate the table does say "Minimum" not "Must be", but I would still use this table to answer an exam question.


Roger
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: test time

That's half of it. The question (incorrectly) asserts that the EGC and phase conductors must be the same size. They do not.

But the concept of "minimum size" goes one way, and not the other. For example, we are allowed to use a #10 EGC and #12 phase conductors in a 20 amp branch circuit. But we are not allowed to use #12 EGC and #10 phase conductors in a 20 amp branch circuit. The NEC Article (not Table) that prohibits that is 250.122(B).
 