LarryFine
Master Electrician Electric Contractor Richmond VA
- Location
- Henrico County, VA
- Occupation
- Electrical Contractor
Additionally, the grounded phase is supposed to be white (or 'grey') throughout the premises, just as in any other grounded supply. It's also supposed to be opened by disconnects, but unfused (common-trip devices are acceptable).diverdan said:I have several industrial customers with Grounded B Phase Systems. They are 3 phase /3 wire systems. A-B, B-C, A-C = 480 v. A- grnd, C- grnd = 480 v. B- grnd = 0v. Distribution gear should be clearly marked as grounded B phase.
And, of course, you won't. The grounded conductor will be the Y neutral or the A-C CT neutral.I've never seen a grounded b phase system @ 208 or 240 volts.
Added: To correct myself, there are indeed 240v corner-grounded Delta systems.
Last edited: