Can I test ohms on a plug for a sealed sewer pump? How many ohms should there be ? Thank you
You can test for winding continuity. But probably not a lot else.Can I test ohms on a plug for a sealed sewer pump? How many ohms should there be ? Thank you
Thank you. This sealed pump apparently had shorted and melted its neutral in two in the service panel and melted other wires (insulation) close to it. I didn't want to take a chance on having to repair that again if the breaker didn't trip fast enough. I got an ohm reading of 1 to 8 on the 20 M scale but only Overload on a pump right next to it ( from the power prong to neutral prong on the cords). I decided to install a gfi outlet and plug in the pump in question, to hopefully protect the panel. It tripped the gfi immediately. So I told the customer to get a plumber. (When the house was built it didn't require gfi). I still wonder if those ohm readings were telling me it is shorted.You can test for winding continuity. But probably not a lot else.
Thank you. This sealed pump apparently had shorted and melted its neutral in two in the service panel and melted other wires (insulation) close to it. I didn't want to take a chance on having to repair that again if the breaker didn't trip fast enough. I got an ohm reading of 1 to 8 on the 20 M scale but only Overload on a pump right next to it ( from the power prong to neutral prong on the cords). I decided to install a gfi outlet and plug in the pump in question, to hopefully protect the panel. It tripped the gfi immediately. So I told the customer to get a plumber. (When the house was built it didn't require gfi). I still wonder if those ohm readings were telling me it is shorted.
Replacing the pump might be the most economical option.Thank you. This sealed pump apparently had shorted and melted its neutral in two in the service panel and melted other wires (insulation) close to it. I didn't want to take a chance on having to repair that again if the breaker didn't trip fast enough. I got an ohm reading of 1 to 8 on the 20 M scale but only Overload on a pump right next to it ( from the power prong to neutral prong on the cords). I decided to install a gfi outlet and plug in the pump in question, to hopefully protect the panel. It tripped the gfi immediately. So I told the customer to get a plumber. (When the house was built it didn't require gfi). I still wonder if those ohm readings were telling me it is shorted.
the customer called a plumber as I suggested. The sealed pit pump float had stuck in "on" position and burned out the motor. The gif tripping immediately meant something was wrong. And it did save my service panel from damage again. Not sure why the breaker didn't trip. Thank you.Replacing the pump might be the most economical option.
A highly-variable reading of several megohms is likely to be the impedance of the technician's fingers.... An ohm reading of 1-8? You should be able to get more precise reading that that. ...
the customer called a plumber as I suggested. The sealed pit pump float had stuck in "on" position and burned out the motor. The gif tripping immediately meant something was wrong. And it did save my service panel from damage again. Not sure why the breaker didn't trip. Thank you.
Your table appears to be for submersible well pumps, OP has a sewer lift pump. Most will have a float switch, and when water is below float you get an open circuit reading, otherwise they often are split phase or capacitor start and reading will include start and run winding as well as capacitor in start winding circuit if it has one.most pump mfgs will give you a cold coil Z spec
usually in the manual
an example