Testing and Verifying Grounding ?

Status
Not open for further replies.

Davebones

Senior Member
Our manufacturing plant was built in 1984 . We have about 150,000 sq ft of manufacturing area plus office space . The structure is metal columns bolted on concrete pads with concrete floors and concrete walls . The metal columns and bar joists are all welded and bolted together . We have quite a few areas with chemical containers which are bonded to the nearest building steel for static charge . Our safety department is inquiring about doing annual testing to verify the bonding and grounding in the plant . ( 1) What kind of testing would be recommended for the static grounds ? ( 2 ) As we have five services into the plant what would we want to do to verify the original grounds and the existing grounding in the plant ? I know we could get a ground tester and use a ohm meter for continuity but as this something we haven't done I want to be sure we use the correct approach to do this ...
 
Low R ohmmeter for connections, 3 pt FOP test for your ground. Any testing company can do that for you and do it right.
 
do you want to test grounding or bonding?

if so, what are your pass/fail criteria?

the NEC criteria is essentially that the connection is made and that can be verified by a visual inspection.
 