I think I favor using using a 6.3 V 2 A 60 Hz filament transformer and a 5 ohm 10 W series resistor.
One transformer lead goes to one end of the 5 ohm resistor. The other end of the resistor and the second end of the transformer secondary are your current limited voltage source. Connect these two output leads to whatever you want to test. One output connection to your hot lead to the fixtures, and the other to either EGC or neutral depending upon what you are testing. The circuit you are testing must be unenergized from any other source. Your load impedance is Zl. The open circuit voltage is Vs and the load voltage is Vl. The constant 5 in the following equation is the 5 ohm resistor and needs to be slightly higher by the amount of equivalent internal resistance of the transfomer. But ignore this because you only need a rough estimate.
Someone else needs to check my math.
Zl = 5/(-1+(Vs/Vl) )
As Vl approaches 0 Zl gets small and approaches 0.
As Vl approaches Vs Zl approaches infinity.
If Zl was 50 ohms and Vs was 6 V, then Vl would equal 5.4545 .
If Zl was 0.5 ohms and Vs was 6 V, then Vl would equal 0.54545 .
.