IEEE and Tyco-Raychem recommend meggering. Don't stop at 1000V, per the test procedures, many problems will not show up @ 1000V. You need to take it to 2500V. I have seen it pass at lower voltage and fail at higher. Twist the bus wires together, and check to braid. Then check from braid to pipe or something that is bonded to ground. Remember to get a hotwork permit if you are in a hazardous area, not just for the megger end, but the whole tracer.
Back to the OP, when the cable is warm, even though it is not energized, high ambient temps or high pipe temps will not give you the inrush current on self-regulating cables that you will get when everthing is cold.
Most plants do their heat trace PM's in October to get ready for winter. That way you have cold mornings, cooler pipes.
If you have to test in summer, can you put cold process in the pipes and turn on the trace to watch in-rush and to verify your GFEP does not trip?