Testing LIM panels

Status
Not open for further replies.

lile001

Senior Member
Location
Midwest
A hospital is asking me about testing their Line Isolation Monitor (LIM) panels. I know that there is an instrument that measures leakage current, and another instrument that creates a simulated leaky load, however I can't find any manufacturers who make such instruments. Can anyone suggest a manufacturer?
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
To go along with Brians post, we normally use Square D's field services to test and commission our ISO panels, but that is due to the fact that we usually use their panels.

Roger
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
brian john said:
My friend use to be a Square D employee, went out on his own several years ago.

Makes sense, we have an independent tester that has basically done the same thing.

We also do our own testing on existing installations but it is somewhat a "conflict of interest" on new installs so we contract it out.

Roger
 