What I'm wodering is how other people around the country do ground testing in gravel pits. What type of equipment / method do you use? More specifically, what type of meter do you use to measure between the reference ground and the motor frames?
Here's how I do it: first, I test the rod(s) at the incoming service using the 3 point fall of potential method. Once this rod has been checked and proves to be an acceptable ground, (it typically measures less than 1 Ohm) this ground rod then becomes my reference ground. Next, I use the same ground testing instrument wired for the "2 point bonding" test and proceed to check the resistance (bond) between all the motor frames back to the reference ground. To do this I take a long length of #12 and run it out from my test instrument (which is still connected on one side to the reference ground rod) and clip it to the motor frame being tested. Now I take my reading and then subtract my lead resistance to determine the true resistance back to the reference ground rod. After subtracting the lead resistance a well grounded / bonded motor will measure less than .1 Ohms.
That, anyway, is how I do the test.
I would be very interested to learn what other methods or equipment are used for this type of testing.
Thanks!
Uncle Bill (my first post, by the way...)
Here's how I do it: first, I test the rod(s) at the incoming service using the 3 point fall of potential method. Once this rod has been checked and proves to be an acceptable ground, (it typically measures less than 1 Ohm) this ground rod then becomes my reference ground. Next, I use the same ground testing instrument wired for the "2 point bonding" test and proceed to check the resistance (bond) between all the motor frames back to the reference ground. To do this I take a long length of #12 and run it out from my test instrument (which is still connected on one side to the reference ground rod) and clip it to the motor frame being tested. Now I take my reading and then subtract my lead resistance to determine the true resistance back to the reference ground rod. After subtracting the lead resistance a well grounded / bonded motor will measure less than .1 Ohms.
That, anyway, is how I do the test.
I would be very interested to learn what other methods or equipment are used for this type of testing.
Thanks!
Uncle Bill (my first post, by the way...)