What is your guys standard procedure for checking motors? We do a lot of farm work, mostly 480 3 phase motors from little stuff up to 500HP or so. I bought my Fluke 1507 a year or so back and have had great luck with it so far. What happened today: Went out to check a 75HP centrifugal pump, they said the breaker was tripping but the wire insulation at the terminations is pretty cracked. Megged motor(at 1000v) just for giggles and it read about 3.5 gigs and up on each of the 3 motor leads to ground. Good. Then replaced the wire/conduit per the customers request, went to fire the motor(literally:rolleyes:) and the smoke rolled out of it.

I guess my question is do I need to be checking ohms between motor leads as well as megging to ground? After it smoked, I checked continuity between motor leads and got 0. Windings shorted together?
 

Kdog76

Senior Member
Typically I would check the motor leads (or motor branch circuit conductors) with a clamp-on ammeter with the motor running, and check my readings against the nameplate full-load current of the motor with the motor fully loaded. Among other things, the driven equipment (including pulleys, belts, bearings, wheels, and such) should be given a once over to ensure it's nothing mechanical in nature causing the overload.

However, when you see smoke pouring out of the motor, its a pretty safe bet those windings are shot...Maybe the motor overload was set too high (if there was one. If not you may consider installing either a motor overload unit or finding a motor with a built-in thermal overload. It would prevent burning up another motor.) BTW, what's the pump's job here?

Also, I wouldn't be too concerned about the insulation cracking, doubtful (but possible) that the cracked insulation would cause the motor to overheat. I think you are correct that the windings may be shorted out. Before installing a new motor, make sure you've got some sort of overload protection on that new motor.

You may find a shop that can rebuild that motor, or you may have to consider replacing it, but you will need motor overload protection here...
 
Last edited:

Zed

Member
If there are no obvious mechanical causes, the very first electrical test I do when a motor trips out on overload or blows a fuse is to check between windings as far back in the circuit as possible, usually at the fuse block or overload.
If all three results are exactly equal then I check insulation resistance.
Keep in mind the motor windings are basically a dead short like transformer windings so the readings will be very low, but they must be exactly the same. Even a difference of lets say 1 ohm to 1.2 ohms is enough to trip the overload and the motor needs a rewind.
If however the motor trips out on a regular basis and the windings are balanced (equal ohmic readings) then I would use my current clamp and check for over current and/or equal current flowing in each phase.
 

Zed

Member
If there are no obvious mechanical causes the first test I do when a motor trips out or blows a fuse is to check the ohmic readings between the motor leads as far back as possible, usually at the overload or fuse block.
Keep in mind the windings are basically a short circuit like a transformer winding so the value is very low but they MUST be exactly equal.
Even a difference of value of lets say 1 Ohm between 2 legs and 1.2 Ohms between the other legs is enough to trip an overload and the motor needs a rewind.
If the windings are balanced (equal ohmic readings between windings) then I check insulation resistance between each leg and then each leg to ground.
If a motor runs but trips out regularly I use the current clamp to check for overloading and/or equal current flow in each leg.
 

Kdog76

Senior Member
If all three results are exactly equal then I check insulation resistance.

I may be a bit weak in this area - I assume you are referencing using a megger? I have limited experience here, so I could use any input on how and when to check insulation resistance. It's one thing I've never used to troubleshoot motors...
 

charlietuna

Senior Member
A motor of this size is gonna read zero resistance between windings due to the motor's wire size. I check the mechanical load to make sure it isn't locked up or being tripped by an external problem. I then meggar each winding to ground at the peckerhead-this being a 480 volt source i would use 1000 volt meggar voltage. Now, this isn't going to tell you if the motor has an internal short between windings(phase to phase), but not to ground at that time. From what occured, i'm assuming the windings were not grounded-but shorted phase to phase--and after it smoked it was no doubt grounded too.. it happens..
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
Typically I would check the motor leads (or motor branch circuit conductors) with a clamp-on ammeter with the motor running, and check my readings against the nameplate full-load current of the motor with the motor fully loaded. Among other things, the driven equipment (including pulleys, belts, bearings, wheels, and such) should be given a once over to ensure it's nothing mechanical in nature causing the overload.

That's what I usually do when they run, but this thing let the smoke out as soon as the 480 hit it.

However, when you see smoke pouring out of the motor, its a pretty safe bet those windings are shot...Maybe the motor overload was set too high (if there was one. If not you may consider installing either a motor overload unit or finding a motor with a built-in thermal overload. It would prevent burning up another motor.) BTW, what's the pump's job here?

Motor had overloads and I believe they were set correctly. Pump is one of three feeding a manifold that feeds irrigation circles.

You may find a shop that can rebuild that motor, or you may have to consider replacing it, but you will need motor overload protection here...[/QUOTE]

Got it, the farmer will rewind/replace the motor and hopefully be back in business. Thanks.

If there are no obvious mechanical causes the first test I do when a motor trips out or blows a fuse is to check the ohmic readings between the motor leads as far back as possible, usually at the overload or fuse block.
Keep in mind the windings are basically a short circuit like a transformer winding so the value is very low but they MUST be exactly equal.
Even a difference of value of lets say 1 Ohm between 2 legs and 1.2 Ohms between the other legs is enough to trip an overload and the motor needs a rewind.
If the windings are balanced (equal ohmic readings between windings) then I check insulation resistance between each leg and then each leg to ground.
If a motor runs but trips out regularly I use the current clamp to check for overloading and/or equal current flow in each leg.

Sounds like I need to start testing the windings. Another one just 2 weeks ago I had a 50 kva transformer that was also tripping the breaker at startup with no load on the secondary. Megged fine and had only been in service 6 mos. Replaced transformer and all is well. I figured shorted windings on this one too. I'll try ohming one next time and see if it tells me anything. I don't like having to throw a 480v breaker into a dead short for testing...there's gotta be a better way to do this.

Thanks.:)

I may be a bit weak in this area - I assume you are referencing using a megger? I have limited experience here, so I could use any input on how and when to check insulation resistance. It's one thing I've never used to troubleshoot motors...

My Fluke 1507 has been a very handy tool. If you do service, especially checking wiring and motors, you should definitely have one. I probably use mine about 3 times a month or so. Up until these last two weeks with the transformer and this motor it's made it obvious where the problem was.

Just a couple examples:

We do work on a large dairy utilizing four small motors to drive a carousel for milking cows. With the wet environment a dairy is, motors and wiring seem to be getting checked and replaced on a regular basis. Being able to isolate the VFD from the wire from the motor, testing each one is invaluable. Right then and there you know which one is testing poorly and needs replacing. No guessing why the drive is showing ground fault.

One about 3 weeks ago, pump panel is blowing one of the two control fuses. Meg the control wire on that side of the fuseblock, it's reading zero. Disconnect starter coil, still reading zero. Pull wires off of HOA/start button, meg again, reads great. Put megger lead on individual wiring terminals of the HOA, reads great. Throw it on the start button, one terminal shorted to ground, couldn't physically see the problem but the Megger caught it. Put the T+ Pro tester on it just for curiousities sake and it didn't show continuity. I would of needed a handful of control fuses to get this one sorted out without the megger if I was just using a regular multimeter.

Sorry for the long post.:smile:
 
Last edited:

zog

Senior Member
Location
Charlotte, NC
Here are the required NETA tests:

Electrical Tests ? AC Induction Motors and Generators
1. Perform resistance measurements through bolted connections with a low-resistance ohmmeter, if applicable, in accordance with Section 7.15.1.1.
2. Perform insulation-resistance tests in accordance with ANSI/IEEE 43.
1. Motors larger than 200 horsepower:
Test duration shall be for ten minutes. Calculate polarization index.
2. Motors 200 horsepower and less:
Test duration shall be for one minute. Calculate the dielectric-absorption ratio.
3. Perform dc overpotential tests on motors rated at 1000 horsepower and greater and at 4000 volts and greater in accordance with ANSI/IEEE 95.
4. Perform stator resistance test phase-to-phase.
*5. Perform insulation power-factor or dissipation-factor tests.
*6. Perform power-factor tip-up tests.
*7. Perform surge comparison tests.
8. Perform insulation-resistance test on bearing pedestal in accordance with manufacturer?s published data, if applicable.
9. Test surge protection devices in accordance with Section 7.19 and 7.20.
10. Test motor starter in accordance with Section 7.16.
11. Perform resistance tests on RTDs.
12. Verify operation of the motor space heater, if applicable.
13. Perform a rotation test to insure correct shaft direction.
14. Measure running current and evaluate relative to load conditions and nameplate full-load amperes.
*15. Perform vibration baseline test.
 