. . .hope that the Rate of rise goes off before . . .
. . .hope that the Rate of rise goes off before . . .
Here's another citation
http://www.patentstorm.us/patents/5450066-claims.html
that talks about rate-of-rise sensors.
Their test method trips the sensor very fast because the rate of temp rise is much faster.
That's the risk; they use commonly available heat sources that can deliver temps way above these trip points, so instead of cooling the heat source they reduce the time the sensors are exposed to these high temps.
Instead of shielding the hi-temp nonresetable detector, you might make a cardboard funnel to focus only on the rate-of-rise detector.
Assuming you can't do the shielding or funneling, if you have a heat source that puts out less than 130 degrees F you will never trip the non-resetable hi-temp sensor.
To give some safety margin, let's say max 120 F.
Assuming a room ambient of 75 degrees F.
120-75 = 45 degree F rise in temp.
45/(>15) = <3 minutes to get to 120 F.
Using this cooler heat source the rate-of-rise detector should trip in less than 3 minutes. The air from a partially-constricted vacuum cleaner exhaust is probably hot enough to do this. You don't have to worry about air speed with this as long as the air temp at whatever speed it's delivered is around 120 F.
If a working unit doesn't trip within 3 minutes, I assume because the rate-of-rise detector response time is too slow, and you can't use shielding or funnels, then I don't see any totally safe way to test the rate-of-rise sensor. And there may
be none, otherwise they might have had you try lower temp settings on the hair dryer.
If you have the 194 F sensor, you can change these numbers around and have a lot less risk of tripping the 194 F sensor.
I hope these things don't have nuisance tripping on hot days in southern climates, or because they are mounted on a ceiling that is the floor of an uninsulated attic.