testing wire integrity
ismaelbucio
New member
Las Vegas
How can you test the wire integrity before connecting to main line power, I am putting 120/208 three phase and I would like to test before connecting main power. I learn how to use the megger but I don't have one, and I would like to use my volt meter and put it in Ohms or Continuity and go from there but I am not exactly one hundred percent sure any tips?
maghazadeh
Campbell CA
The only test you can do at this time is insulation resistance test, which that is accomplished by applying voltage for a certain amount of time to the wire. Megger does generate voltages needed to do this test, but a normal volt meter is not a right tool for that.
kwired
Electron manager
NE Nebraska
A regular meter will not do an insulation test, it is still a good idea to at least do a continuity check in case there is a short circuit or ground fault before turning power on. Any continuity where it does not belong is a bad thing, and you especially would not want to be plugging in a POCO meter while live if that is the case. (Even though you are not supposed to plug meters in while live)
gndrod
Ca and Wa
OJT
OJT
Depending on the extent of testing a BC or complete system, a hi-pot test would best check the conductor insulation strength for any dielectric weakness or damage that may exist against a complete grounded/grounding system. i noticed your profile of possibly being in an USAF affiliate, you may have an opportunity to get into a training program that may have available hi-pot testing of both aircraft and Ground support equipment cabling validation. (Note that hi-pot levels can have breakdown results from improper test settings.)
K8MHZ
Some cables will have their warranty voided if a hi-pot test is done on them. Technically, it is a form of destructive testing.
I would check with the mfg. of the cable before doing any hi-pot testing.