Hey guys, could any of you tell me how to calculate voltage between points A and B? There's way too many sources and it makes me confused. Thank you :?
Start one step at a time.
The thing which is keeping you from calculating the voltage between A and B based on the current through R2 and the voltage source U2 is the parallel combination of the 4 and 5 sources and resistors.
But you can take that part of the circuit and break it at the top and bottom (at points I will call C and D) and figure out what the Thevinin equivalent of that pair would be.
How do you do that?
1. Assume an open circuit between C and D (except for the four elements in the two parallel paths.) You can then calculate the voltage, knowing that I4 and I5 will be of the same magnitude.
2. Now place a short circuit between C and D and calculate the current that will be flowing in that wire. That, combined with the voltage from 1 will tell you what the Thevinin resistance of the C-D network is.
Make that replacement in the circuit diagram.
The result, with no load from A to B, is simply a circular loop in which all of the currents must be equal. That will allow you to calculate the current and therefor the voltage drop across R2.
That in turn will allow you to calculate VThAB.
Now the algebra may be messy, so I leave that part to you. :D
Test your result by plugging in simple values for the U's and R's to see that you get the right answer for special cases. If you do, it makes it probable that you got the whole thing right.
Smart $
Esteemed Member
Ohio
Edit: Phooey, still small.:(
GoldDigger
Hi Kamil,
Once you have calculated the Thevenin equivalalent (both voltage and resistance) for the C-D network (see my earlier post), please post it so that we can check your work before you go on to the next step. :)
If you are unsure how to do that, let us know, because that part is a pretty simple circuit to find the equivalent of.
Smart $
Esteemed Member
Ohio
Hi Kamil,
I think you are overthinking this... :angel:
Smart $
Esteemed Member
Ohio
Depends on whether or not you are allowed to leave I2 in the answer.
( since I2 is not an independent variable.)
If that answer is acceptable, then just stating that Vth =Vth would be just as satisfactory. :)
All In values are dependent variables. You cannot state an equivalent (other than the one you stated) without using one (or more) of these current variables.
GoldDigger
Actually you can.
You can eliminate all of the I variables and state the answer entirely in terms of the U and R variables.
I was assuming that was what the instructor (or textbook) was looking for.
Think of it as a practical rather than a theoretical problem:
If you build a circuit using the specified ideal voltage sources (U's) and resistors (R's), do you agree that the currents will no longer be variables. You could either calculate or measure them.
BTW, calling them dependent variables is equivalent to saying that they can be determined knowing only the independent variables.
Perhaps you meant mutually dependent, i.e. each current depends on the others, but that is not the case here.
Or did you mean to say that they are independent variables? They are not.
Smart $
Esteemed Member
Ohio
Actually you can.
Yes, I know we can... but why, when it is so much easier stating the answer with an In variable. Now if there were restrictions placed on the answer format, that'd be a different matter... and seemingly what you want to do when there is no need.
Also, I meant dependent variable. All In values are dependent on all Un and Rn values.... no different than E=IR.
GoldDigger
Ye------
My point exactly. If all of the I variables are dependent variables, why use one of them to write the answer?
If I asked you for the voltage between points A and B of the circuit shown but with all of the components except U2 and R2 removed, would you accept the answer
Vth = U2 - I2R2, or would you rather have me just say Vth = U2? :)
Electric-Light
Did you Google at all? Many of us are happy to help fellow member, but I personally like to see you put in some effort to try to figure it out rather than post what looks like a homework problem and ask "how do you get the answer xx ? "
Smart $
Esteemed Member
Ohio
But you can't remove all the other components. I2 is dependent on them. Vth = U2 + I2R2 is an acceptable answer when there is no restriction on answer format.
GoldDigger
I was not saying that would be a useful step in the real problem, I was posing an alternate, much simpler problem in which you could trivially calculate I2.
For the trivial problem, I can remove I2 because it is zero in the open circuit case. For the OP's problem I can construct a formula that contains no I values at all, just U and R.
One more argument about why my interpretation may not be the only "acceptable" one but is certainly a more useful one:
With your answer, if someone asks the question of how the value of Vth varies as you change the value of U5, for example, your answer does not give you a clue. My answer would. (At least the limiting behavior for large values of U5 would be clear, even if the formula is messy.)
And lets take it in a slightly different direction: If the problem asked instead for the value of Rth, your formula would be totally useless
since the current through a short between A and B would not be I2.
With my (not yet constructed) formula you would have a voltage that is expressed entirely in U and R values and you could pair that with the short circuit current expressed entirely in U and R values and combine them to calculate Rth.
If you were trying to give a very quick answer to a complex problem on a multiple choice test, you could hope that your answer was one of the ones offered. If it was, then the instructor felt just as you do about it. :happyyes:
But it does not really serve the purpose for a homework question intended to exercise the general process of calculating Vth and Rth in a complex circuit.
I hope we get more feedback from the OP at some point as to what the instructor was trying to get.
PS: In the drawing shown, if I2 is taken to be positive in the direction shown by the arrow next to it, then the voltage will be U2 - I2R2 not U2 + I2R2.
Smart $
Esteemed Member
Ohio
I acknowledge your points...
KamilAussie
KamilAussie
Of course I googled first. I'm a total beginner so it didn't help me.
Thanks for your advice, I appreciate it. I'll go through all of them in the evening and try to solve it! I'll let you know what I've got!
Have a good one ;)