B bphgravity Senior Member Location Florida Mar 8, 2005 #3 Re: thankyou Originally posted by pipeit: ...am i correct that after finding FLC for the above motors i need to adjust for the actual voltage... Click to expand... No, read the sentence below the Table heading. The voltages listed are rated motor voltages. The currents listed shall be permitted for system voltage ranges of 110 to 120, 220 to 240, 440 to 480, and 550 to 600 volts. Click to expand...
Re: thankyou Originally posted by pipeit: ...am i correct that after finding FLC for the above motors i need to adjust for the actual voltage... Click to expand... No, read the sentence below the Table heading. The voltages listed are rated motor voltages. The currents listed shall be permitted for system voltage ranges of 110 to 120, 220 to 240, 440 to 480, and 550 to 600 volts. Click to expand...