A long long time ago in ancient history, there was fluorescent lighting; first with magnetic ballasts, then electronic. And THD (Total Harmonic Distortion) was important. Most specs called for a THD <10%. THD has not gone away (never will), but its importance in 'LED Land' seems to have all but vanished. You can hardly find a manufacturer who publishes the data. While a <10%THD is possible with LED drivers, the norm is <20%. (<10% 'appears' to have limitations: 120V higher - input loads, 277V - lower inputs (20W / 30W seems to be the threshold), and the actual (programmed) load, vs. the maximum load of the driver has a significant impact also...)
What gives?
We had to have <10%, but OOPS(?) <20% is OK? The utility companies have gotten better at dealing with THD?
I have a larger project where the clients' boiler plate calls for <10% on ALL fixtures. While possible, it's a challenging, has additional cost...
I cannot just tell the client: "oh... nobody cares about that anymore"; I need some real back-up.
Any direction / suggestions will be greatly appreciated in advance,
m.
What gives?
We had to have <10%, but OOPS(?) <20% is OK? The utility companies have gotten better at dealing with THD?
I have a larger project where the clients' boiler plate calls for <10% on ALL fixtures. While possible, it's a challenging, has additional cost...
I cannot just tell the client: "oh... nobody cares about that anymore"; I need some real back-up.
Any direction / suggestions will be greatly appreciated in advance,