Zero.Any ideas on what ideal values should be for THD?
At 23% that had better not be voltage.And... are we talking VOLTAGE THD or CURRENT THD?
Any ideas on what ideal values should be for THD?
For instance, I've received a report and the number 23 appears consistently.
Any guidance on desired values would really be appreciated.
NB. All values were calculated using a Fluke 434.
Bingo.Read IEEE 519.
But when it all said and done, it depends on your entire system. I have had applications where multiple thousands HP motors were fed off generators line. we were creating 30% to 50% THDi and more than 10% THDv. These may seem too high but we were completely isolated from utility and everything on our line (VFDs, transformers, reactors, generators...) were rated for that much harmonics, so nobody cared.
But if you're connected to the grid, you have neighbours. Maybe not close but the the PCC makes them neighbours in that sense.Bingo.
Super condensed version of IEEE 519:
"Thou Shalt Not Screw Up Thy Neighbor's Voltage!"
No neighbors, no problem!
Does the telephone exchange have large rectifiers? I've come across a few that do.In one Telephone exchange, current THD was within limits, but voltage THD was slightly off limit. The POCO was trying to put the blame on us and also penalty. I am about to write an objection letter to them.......
Yes. The telephone exchange has large SMPS rectifiers.Does the telephone exchange have large rectifiers? I've come across a few that do.
Large as in?Yes. The telephone exchange has large SMPS rectifiers.
19X100A DC-1NOLarge as in?
And how many?
Not huge but in combination that could be your problem.19X100A DC-1NO