So I have a quote to put in one maybe four Tesla lvl2 charger. It's a condo with (8) 70a meter and one common. 400a main single ph 240v
I calculate my unit to be using 54a @
1300 ft^2 with electric dryer
If I put in the 30a charger I calculate I need 64a =) so 70 ok
If i put in the 40a charger I calculate I need 67a
I have never calculated the disco on these multi bank meters
If put in 3 40 amp teslas and they're all within 70 subeeds then the 400 amp main must be still plenty good
Question is how do you calculate the main breaker for the The multibank multifamily application
Thanks!