This question arises from time to time:
"Why does the delta diagram include 60 degree angles when the phase separation is 120 degrees?"
Look at it this way:
Say you wire up 3 secondaries into a wye configuration, and to impress the Boss, you draw out the wye phasor diagram complete with arrows.
Now the Boss comes along and says, "Dummy, that is supposed to be a delta!" You sheepishly correct your mistake. Now how do you correct your phasor diagram?
You merely slide the arrows around until you have formed a triangle. You do not change the directions of the arrows! You now have the familiar delta phasor diagram which is an equilateral triangle with internal angles of 60 degrees. The phase separation however is still 120 degrees.
If you know a little trig, you can see that the voltage of any one side is,
V = 2 x Vphase x cos(60) = Vphase
Of course that is obvious since we have an equilateral triangle.
For the line to line voltage in a wye, we use the same approach but the angles are different, 120, 30, 30.
Then Vline-line = 2 x Vphase x cos(30) = 1.732 x Vphase