In 240.21 C. It discusses some rules for conductor ocp on transformer secondary's. At the end of the paragraph it states- "The provisions of 240.4(B) shall not be permitted for transformer secondary conductors. 240.4(B) is the section that allows you to go to the next ocpd size up to 800A as long as the conditions stated are met. My problem is that on a one line I'm pulling wire for, there is a 800A switchboard being fed from a transformer secondary with two parrallel sets of 500 kcmil. I think the wire is undersized, but everyone else thinks I'm wrong and that the code in question has nothing to do with my question. Any opinions would be cool.