Re: The Count Is In
Section 110.9 requires fault interrupting OCPDs to ??have an interrupting rating sufficient for the nominal circuit voltage and the current that is available at the line terminals of the equipment.?
Ordinarily this is a good idea. There are however, several distribution system configurations where the OCPD will never possibly have to interrupt ??the current that is available at the line terminals of the equipment? or the probability is literally so low as to be impossible.
The result is that some equipment must have an interrupting rating much higher than necessary- in some cases higher than is available.
This applies typically to large power distribution equipment; although it can apply to some forms of transfer switches.
API has been proposing changes to the text for several cycles now primarily because these distribution schemes are very common in refineries. CMP1 ultimately refers it to 90.4 and, as I said, it is ?beyond the average AHJ's ability to understand - let alone rule on correctly.? API, on the other hand, doesn?t want it to be an ?engineering supervision? issue. The bulk of the API NEC Task Force are engineers, although a few are ?operators.? However, many of them are not PEs and they believe an ?engineering supervision? clause would require PE certification of the design.