The differenece ground wires

Status
Not open for further replies.
Re: The differenece ground wires

One is stranded the other is solid :)

I believe the NEC requires #6 and larger to be stranded though we do have a coil of #6 solid TW insulated (in telephone gray I might add) ground wire that we use to ground TELCO protectors and equipment.

-Hal
 
Re: The differenece ground wires

I believe the NEC requires #6 and larger to be stranded
I have never heard of this requirement?

250.62 allows both with no restriction on size for grounding electrode conductor.

250.118(1) allows both with no size restriction for equipment grounding conductor.
 
Re: The differenece ground wires

Section 310.3 states, "where installed in raceways, conductors of size 8 AWG and larger shall be stranded."

The Exception then states, "as permitted or required eleswhere in this code".

Grounding conductors would be one of those exceptions.

[ October 25, 2004, 10:32 AM: Message edited by: bphgravity ]
 
Re: The differenece ground wires

Yup, that's what I was thinking of. If I had gotten up off my butt and looked in the book I could have quoted it correctly! :eek:

-Hal
 
Re: The differenece ground wires

"As permitted or required elsewhere in this code" - one example is solid 8 AWG used in raceways for pools, as we us a lot of solid 8 AWG, so they relax the Chapter 3 requirement somewhat.

Pierre
 