The history of 314.16?

Status
Not open for further replies.

Kimura

Member
Location
Delaware
Just curious: When did 314.16 (box fill requirements) enter NEC? Have they become more stringent overtime or unchanged since the introduction ?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Table 3.-Cubic Inches Per Conductor is the same in the 1940 NEC as it is today with the exception of not including #6 AWG conductors. This is from the 1940 NECH:

1940 NEC Conductors.jpg
 

tortuga

Code Historian
Location
Oregon
Occupation
Electrical Design
It got added in the 1933 NEC, there is a table like the one infinity posted in the 1935, I dont have a copy of the 1933 but you can access the meetings proceedings on the NFPA's website under the 1933 NEC.
Before 1933 boxes in general had to be at least 1-1/2 inches deep, there were exceptions for pancake boxes etc.
The requirement that plaster be repaired around boxes and unused openings be closed goes back much farther than that.
Before 1928 boxes were not required at lighting outlets, and were mainly used with black rigid conduit and AC cable, since conduit fill with rubber wire was so restrictive there probably was not a easy way to 'overfill' an octagon box on a conduit system.
 