Most small conductors (i.e., No. 6 AWG) are not protected against short circuit conditions. NEC 240.1 and 110.10 requires that the OCPD clears the fault without extensive damage to the conductor. Also, the last paragraph of 110.10 states "listed equipment applied in accordance with their listing shall be considered to meet the requirement of this section." So, If we have a No. 6 conductor (listed) unprotected against short circuit conditions (i.e., available current is 20 kA for 1 cycle and withstand rating is only 10.7 kA according to ICEA for 1 period) will this last paragraph of 110.10 allow this misapplication?