Question for those knowledgeable in PV systems and Line Side Connections.
I have been beating the code for the past couple of days trying to wrap my head around 690.64(A), 690.14(C),(D), and Article 230. I have seen others on this forum, and other articles, state that when making a line side connection that the PV disconnect is part of the Utility's Service Rule of 6.
I am having a hard time understanding why this is. Is this not a Second Service as allowed by 230.2(A)(5)? 230.40 Excp. 5, and 230.82(5) also imply that this is a second service (or at least to treated as such). At the very least since we are following 690.64(A), this points to 230.82 and these conductors are clearly on the line side, we can say these are service conductors.
Now as I read 230.71(A), we are allowed up to 6 service disconnects PER service. I believe we clearly have a second service, so why are we not allowed up to 12 Disconnects (2 Groups of 6, 6 for utility service and 6 for Parallel Generation Service)?
In terms of the intent of the code, lets consider a building with a single main service disconnect with no PV system installed. In order to shut down the building, you flip the main service disconnect. Now if we add the PV system as a line side connection, you still only need to flip the main disconnect. Flipping the PV system disconnect has no effect on the building. The Utility service is still there powering the service conductors. Turning off the PV disconnect de-energizes nothing!
Please, some one tell me the code reference I am missing so I can put this issue to rest. I just don?t see where in either the text of the code or the intent of the code that it says that the PV disconnect is part of the Utility?s service disconnect.
Thank you!
I have been beating the code for the past couple of days trying to wrap my head around 690.64(A), 690.14(C),(D), and Article 230. I have seen others on this forum, and other articles, state that when making a line side connection that the PV disconnect is part of the Utility's Service Rule of 6.
I am having a hard time understanding why this is. Is this not a Second Service as allowed by 230.2(A)(5)? 230.40 Excp. 5, and 230.82(5) also imply that this is a second service (or at least to treated as such). At the very least since we are following 690.64(A), this points to 230.82 and these conductors are clearly on the line side, we can say these are service conductors.
Now as I read 230.71(A), we are allowed up to 6 service disconnects PER service. I believe we clearly have a second service, so why are we not allowed up to 12 Disconnects (2 Groups of 6, 6 for utility service and 6 for Parallel Generation Service)?
In terms of the intent of the code, lets consider a building with a single main service disconnect with no PV system installed. In order to shut down the building, you flip the main service disconnect. Now if we add the PV system as a line side connection, you still only need to flip the main disconnect. Flipping the PV system disconnect has no effect on the building. The Utility service is still there powering the service conductors. Turning off the PV disconnect de-energizes nothing!
Please, some one tell me the code reference I am missing so I can put this issue to rest. I just don?t see where in either the text of the code or the intent of the code that it says that the PV disconnect is part of the Utility?s service disconnect.
Thank you!