I had a classmate ask a question yesterday at school.

"If you install a 3-phase (with a neutral) disconnect do you need to disconnect the neutral with the hot-legs.? Or can the Neutral go straight to the Load bypassing the disconnect." ??
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
stgeorge said:
I had a classmate ask a question yesterday at school.

"If you install a 3-phase (with a neutral) disconnect do you need to disconnect the neutral with the hot-legs.? Or can the Neutral go straight to the Load bypassing the disconnect." ??

A solid neutral is the norm.

Roger
 

C3PO

Senior Member
Location
Tennessee
stgeorge said:
I had a classmate ask a question yesterday at school.

"If you install a 3-phase (with a neutral) disconnect do you need to disconnect the neutral with the hot-legs.? Or can the Neutral go straight to the Load bypassing the disconnect." ??

Roger is correct the Nuetral does not have to be disconnected but it does have to run with the ungrounded conductors(hot-legs).
 

ultramegabob

Senior Member
Location
Indiana
stgeorge said:
I had a classmate ask a question yesterday at school.

"If you install a 3-phase (with a neutral) disconnect do you need to disconnect the neutral with the hot-legs.? Or can the Neutral go straight to the Load bypassing the disconnect." ??

where would you buy a 4 pole disconnect?
 

ultramegabob

Senior Member
Location
Indiana
I have seen alot of 4 pole contactors, but never a 4 pole disconnect that I can recall, what is an application that would require that?
 

C3PO

Senior Member
Location
Tennessee
ultramegabob said:
I have seen alot of 4 pole contactors, but never a 4 pole disconnect that I can recall, what is an application that would require that?

I guess if you need to switch the nuetral for some reason. Square D also makes a 6 pole but only in NEMA 4X or NEMA 12/3R enclosures. Not sure of an application for it though.
 

Buck Parrish

Senior Member
Location
NC & IN
stgeorge said:
I had a classmate ask a question yesterday at school.

"If you install a 3-phase (with a neutral) disconnect do you need to disconnect the neutral with the hot-legs.? Or can the Neutral go straight to the Load bypassing the disconnect." ??


If it is a three phase Service you have to bond the neutral to the can. Terminated, then run through to the load.
 

POWER_PIG

Senior Member
nakulak said:
would you happen to know the code section for this please ?
Hmmm I know a genny is not considered a seperatly derived system unless the utility neutral is opened during transfer, 250.20 d1..... maybe thats what hes refering to,,,,,,,,I dunno, Im gonna go look again.
 

haskindm

Senior Member
Location
Maryland
nakulak said:
would you happen to know the code section for this please ?

Article 100 - definition of "separately Derived System" states that a separately derived system shall "have no direct electrical connection, including a solidly connected grounded circuit conductor, to supply conductors originating in another system." This would require a 4-pole transfer switch in a 3-phase system. Also 514.11 motor fuel pumps require that the grounded conductor be disconnected along with the "hot" conductors. This would require a 4-pole switch on a 3-phase pump.
 