This will change in 2017 if the first draft stands...the proposed rule will require a full arc flash calculation.
I can't even get a load side terminals available fault current figure from most POCO I deal withThat would be interesting. Especially since the line side of the service disconnects are tough to calculate without clear input from the utility on their upstream protection.
A good qualified person also knows to some extent that if they are at the end of a long run, or at a location with smaller source that the levels are somewhat low, and also knows if there is a larger source that the closer they are to that source the higher the incident energy will be (in general).This comment has little to do with whether or not such markings are needed - just a statement that those that are qualified will have some idea of what is going on, and a non qualified person has no clue in this area.
Yes, I understand that is the most difficult point on the system to get the required information to do an arc flash calculation, but the following is from the first draft report.That would be interesting. Especially since the line side of the service disconnects are tough to calculate without clear input from the utility on their upstream protection.
110.16(B) Service Equipment.In addition to the requirements in (A), service equipment shall contain the following information:
- Nominal system voltage
- Arc flash boundary
- At least one of the following:
- Available incident energy and the corresponding working distance
- Minimum arc rating of clothing
- Site-specific level of PPE
...what good is it to further break down the hazard level?...
It is my opinion that this is additional CYA to protect you from the stupid. Not the stupid from an arc flash.:slaphead:
How am I assured the information on the label is accurate to begin with? Codes may require that new calculations be made when certain changes are made - but as mentioned earlier it is often hard to even know what the impact is on the POCO primary side - and even if we do know, they can change things at any time and then the labels are incorrect.It is my opinion that this is additional CYA to protect you from the stupid. Not the stupid from an arc flash.:slaphead:
Exactly my argument against such labeling. Maybe things are different in different parts of the country, but around here nearly nobody would understand any of that information other then those that do the calculations. (I won't even say those that affix the label necessarily understand). Go to an industrial plant where they have fairly complex safety program (especially including electrical safety and use of 70e) and maybe it is useful, everywhere else around here it is the contractor, designer, and/or electrical inspector that pay any attention to such labels. May be a poor attitude to take on this topic but that is the reality I am seeing.Does the average person who would benefit from this label, understand what any of the information presented on it even means?