Hey all,
Studying for my masters and came up with a question. So for circuits rated less than 800 amps, you are allowed to use the next size up rule to size your overcurrent protection of the circuits conductors. so lets say i have a 500 amp non-continuous load with 75 degree terminals and i want to feed it with parallel conductors. 4/0 is rated at 230 amps and a pair of them would be rated at 460 amps. Would i be allowed to apply the "next size up" rule since there isnt a standard fuse or breaker that corresponds to this amperage? (which would allow me to run paralleled 4/0 conductors to feed the 500 amp)
Studying for my masters and came up with a question. So for circuits rated less than 800 amps, you are allowed to use the next size up rule to size your overcurrent protection of the circuits conductors. so lets say i have a 500 amp non-continuous load with 75 degree terminals and i want to feed it with parallel conductors. 4/0 is rated at 230 amps and a pair of them would be rated at 460 amps. Would i be allowed to apply the "next size up" rule since there isnt a standard fuse or breaker that corresponds to this amperage? (which would allow me to run paralleled 4/0 conductors to feed the 500 amp)