Update
Update
Two generators, one stationary 150KW, one 200KW trailer mounted, stationary generator is connected to 3pole automatic transfer switch, trailer mounted generator is back feeding load side of 400amp breaker (double lug) on stationary generator. There is a #10awg green wire connected to the frame of the trailer mounted generator, the other end is connected to the equipment ground lug on the stationary generator, anyone see any problems with this?
Some things have changed in the past couple of days:
1) #10awg changed to #6awg, I am being told that the generator is grounded properly according to 250.34
2) Grounding electrode added
3) Ohmic test done between trailer and grounding electrode. This is what was said:As with grounding terminal connections, proper bonding of the neutral terminal of a power receptacle may be confirmed via testing by a
competent electrician with the correct equipment, and the ohmic resistance should measure near zero and must not be intermittent, which indicates a loose connection.
Below is the testing required for the neutral to ground to verify the ohms. Here is the result of our Ohm test on the 6AWG wire. (0.04 Ohms)
Picture shows someone with meter going from trailer to electrode.
4)I am being told that the grounding is secure, this is what was said:Issue 1: The generator not being properly grounded. According to 29CFR 1926.404(f) on the issue of grounding we see that the a portable generator according to paragraph (b) in the standard. Here is an excerpt from the standard as mentioned
"(i) Portable generators. Under the following conditions, the frame of a portable generator need not be grounded and may serve as the grounding electrode for a system supplied by the generator:
(B) The noncurrent-carrying metal parts of equipment and the equipment grounding conductor terminals of the receptacles are bonded to the generator frame."
Over and above of the standard, the temporary generator is securely connected to the earth ground on the permanently mounted generator which has been grounded according to NEC standards for fixed installation. The temporary generator grounding is secure, independent of the additional earth ground that was placed according to the regulations, but it is not required.
Issue 2: The generator is not properly bonded. The manufacturer has made sure to bond the internal parts of the generator to the frame that covers the other concern.