Thank you this is what i was looking for, could you please give me some code to back up # 3?
This is what i was trying looking to do, i just can't convince the AHJ that it mets code.
Its not in the code as a prescriptive item, it was a suggestion.
Sounds like the AHJ wants smokes up during construction, if he has the discretion that's what you have to do, and here is what you have to do. (assuming the alarm transmits to the FD, after 4 or 5 false alarms and you possibly getting fined for the false alarms, maybe you can revisit it :thumbsup: )
2011 NFPA 72 Section 17.7.1.11* Protection During Construction
17.7.1.11.1 Where detectors are installed for signal initiation during construction, they shall be cleaned and verified to be operating in accordance with the listed sensitivity, or they shall be replaced prior to the final commissioning of the system.
17.7.1.11.2 Where detectors are installed but not operational during construction, they shall be protected from construction debris, dust, dirt, and damage in accordance with the manufacturer’s recommendations and verified to be operating in accordance with the listed sensitivity, or they shall be replaced prior to the final commissioning of the system.
17.7.1.11.3 Where detection is not required during construction, detectors shall not be installed until after all other construction trades have completed cleanup.
Edit: The AHJ, or the adopted code and amendments define whether they need to be there during construction, despite common sense.