bluesprinter
Member
- Location
- kensington maryland. us
- Occupation
- electrician
When is it acceptable to use the residential optional load calculation from the nec. 220.82
I'm adding a evse (vehicle charger) to a existing 200 amp service with the existing typical loads including a heat pump hvac system.
The county permit reviewer for the county is requesting documentation of the load calculation.
when I perform the calculation using the optional methods it comes out to 155 amps on a service rated at 200 amps
I submitted a calculation using 40% derating the furnace of @. 15000kw and he responded back
Heating needs to be at 100%, If heat is supplemented then you need to add 65% of the supplemental heating load unless both don’t work at the same time.
what would be your thoughts and responses that he's not recognizing the option calculation
When I took ibew code class As a student We were told that you use the standard for new properties and the optional for additional loads to existing buildings and homes
but we still must apply 80% of the main overcurrent device rating.
should the load of a evse or other be added after the allowed adjustments in either method of calculation ?
We have i've seen adjustments for led lighting loads vs the 3va per sq foot
Thanks
I'm adding a evse (vehicle charger) to a existing 200 amp service with the existing typical loads including a heat pump hvac system.
The county permit reviewer for the county is requesting documentation of the load calculation.
when I perform the calculation using the optional methods it comes out to 155 amps on a service rated at 200 amps
I submitted a calculation using 40% derating the furnace of @. 15000kw and he responded back
Heating needs to be at 100%, If heat is supplemented then you need to add 65% of the supplemental heating load unless both don’t work at the same time.
what would be your thoughts and responses that he's not recognizing the option calculation
When I took ibew code class As a student We were told that you use the standard for new properties and the optional for additional loads to existing buildings and homes
but we still must apply 80% of the main overcurrent device rating.
should the load of a evse or other be added after the allowed adjustments in either method of calculation ?
We have i've seen adjustments for led lighting loads vs the 3va per sq foot
Thanks