A mod removed my question from the PV forum about the same project for being a duplicate, but actually it wasn't. Here is the question:
I am connecting a 480/277 inverter to a 208/120 service through an autotransformer, which is new for me.
I have done this with a 208 delta to 480/277 wye transformer, and it is obvious in that in that case the neutral on the 480 side must be bonded to ground, but an autotransformer has a neutral common to the primary and secondary sides which is bonded to ground at the service. It seems to me that I should not bond neutral to ground at the transformer in this case. What say you?
It was asked and answered in this thread that this is not a SDS, but does it follow from that that the neutral at the transformer should not be bonded to ground?