to reduce fault current.
Where have those of you that said you've used them found them? All I can find are line reactors to be used in combo with VFD's. Those type do not significantly reduce fault current.
I've got a few situations where we've discovered a lot of our old gear is under rated. I can replace a ton of gear in a few buildings - high $$ and lots of down time, replace the transformers (low impedance single phase cans wired for 3 phase) with new pad mounts - logistically very difficult as these are in below grade vaults plus a host of other issues or add isolation transformers between the existing cans and the MDP's (possible, but with the new DOE regs Jan 1st, not looking viable) or add these impossible to find current limiting 208V line reactors.
Also have the same deal on one service that is 240V ungrounded delta. Transformer sizes required are between 150 and 500KVA if I go that route.
Thoughts anyone?
Where have those of you that said you've used them found them? All I can find are line reactors to be used in combo with VFD's. Those type do not significantly reduce fault current.
I've got a few situations where we've discovered a lot of our old gear is under rated. I can replace a ton of gear in a few buildings - high $$ and lots of down time, replace the transformers (low impedance single phase cans wired for 3 phase) with new pad mounts - logistically very difficult as these are in below grade vaults plus a host of other issues or add isolation transformers between the existing cans and the MDP's (possible, but with the new DOE regs Jan 1st, not looking viable) or add these impossible to find current limiting 208V line reactors.
Also have the same deal on one service that is 240V ungrounded delta. Transformer sizes required are between 150 and 500KVA if I go that route.
Thoughts anyone?