I recently responded to a "explosion" that resulted from a thermal fluid heater at a large bakery. The thermal fluid used in this heater is an oil; Exceltherm 600 with a ignition point of 660 degrees F. The oil is pumped from the heater and through heat exchangers into an oven that is used to heat the clients product.
The heater is not a pressure vessel; it is opened to the atmosphere. Their is an expansion tank located above the heater used as the ballast for the system. The expansion tank then vents into a dump tank located at the floor level. The dump tank vents into the mechanical room; directly to the floor. The vent is located about 8 feet from two air compressors and about 10 feet away from a gas-fired domestic hot water heater.
What happened was an occurence caused the thermal fluid (oil) to form a vapor which was vented from the dump tank into the room. The mechanic noticed white smoke which was most likely the vapor going through a condensing phase. After a few minutes of this white smoke an explosion occurred. Most likely from the ignition of the gas-fired domestic hot water heater or the start up of the air compressors, possible causing a spark.
If I am reading the code correctly, as per NEC 500.5(B)(2), this mechanical room should be classified as a Class I Division 2. Obviously one of my recommendations to the client is to re-pipe the vent to an area outside the room. That being said, what are your thoughts regarding the air compressors and the hot water heater being in the same room?
The heater is not a pressure vessel; it is opened to the atmosphere. Their is an expansion tank located above the heater used as the ballast for the system. The expansion tank then vents into a dump tank located at the floor level. The dump tank vents into the mechanical room; directly to the floor. The vent is located about 8 feet from two air compressors and about 10 feet away from a gas-fired domestic hot water heater.
What happened was an occurence caused the thermal fluid (oil) to form a vapor which was vented from the dump tank into the room. The mechanic noticed white smoke which was most likely the vapor going through a condensing phase. After a few minutes of this white smoke an explosion occurred. Most likely from the ignition of the gas-fired domestic hot water heater or the start up of the air compressors, possible causing a spark.
If I am reading the code correctly, as per NEC 500.5(B)(2), this mechanical room should be classified as a Class I Division 2. Obviously one of my recommendations to the client is to re-pipe the vent to an area outside the room. That being said, what are your thoughts regarding the air compressors and the hot water heater being in the same room?