For short circuit protection on motor applications, the NEC allows you to use a larger value (250% of FLA) when using a Thermal Magnetic Breaker than when using a Time Delay Fuse (175% FLA). Does this mean that you SHOULD use a larger value breaker than you would a fuse?
For example, if I have a motor that is operating well (no nuisance trips) with a class CC fuse sized at 175% FLA, and I want to switch to a thermal magnetic breaker, can I expect it operate just a well at 175% FLA?
Or do no nuisance trips at 175% FLA for a fuse not translate to no Nuisance trips at 175% FLA with a breaker? Does the 250% rating allowance for a breaker only mean that I CAN size it that large and still be safe per the NEC, or should I expect to have to size my breaker larger than a fuse.
Thanks in advance.