Thermocouple NEC

Status
Not open for further replies.

wireday

Senior Member
Location
New England
Occupation
Master electrician
Is there a code section pertaining to TC's. I realize the the TC conductors need to be in separate conduits, They must be allowed in the same control box, Do I need a certain rated TC wire if its around the 120v controller in my control box? I need to run from control box out to point of contact on machine. I would like to read up and understand better.Do they make 600volt rated TC wire?
 
I would never consider running TC conductors or cables with power wiring no matter what the insulation rating of the cable may be. The termocouple single is very sensitive to induced voltages and currents.
 