• We will be performing upgrades on the forums and server over the weekend. The forums may be unavailable multiple times for up to an hour each. Thank you for your patience and understanding as we work to make the forums even better.

Thermocouples Junctions.

Learn the NEC with Mike Holt now!
Status
Not open for further replies.

reyamkram

Senior Member
Location
Hanover park, il
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.
To me that means that neither of the T-couple wires are connected to the metallic housing or cable shield, but the housing and cable shield are connected together. I would guess that the shield should be grounded in the box.
 

4x4dually

Senior Member
Location
Stillwater, OK
Occupation
Electrical Engineer/ Ex-Electrician
Correct. The ungrounded thermocouple means the junction of the two wires in the probe are isolated from the sheath.

Visual stolen from the webs:

Screenshot 2022-03-09 131930.jpg
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
what is a ground drip?
 

garbo

Senior Member
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
At an injection plant & large candy company that I worked out the The thermocouple wires were never grounded. Was taught to only ground one end of shield on cables. If you ground both ends the shield might carry current.
 
Status
Not open for further replies.