Thermocouples Junctions.

Status
Not open for further replies.

reyamkram

Senior Member
Location
Hanover park, il
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
 
WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.
To me that means that neither of the T-couple wires are connected to the metallic housing or cable shield, but the housing and cable shield are connected together. I would guess that the shield should be grounded in the box.
 
Correct. The ungrounded thermocouple means the junction of the two wires in the probe are isolated from the sheath.

Visual stolen from the webs:

Screenshot 2022-03-09 131930.jpg
 
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
what is a ground drip?
 
Hello,

I requested information on the type of thermocouples we have on our injection unit, I received a replay,

WE use unground J thermocouples, the shields are grounded,

Question----dose that mean the thermocouple junction is unground and one end of the shield is ground in the control box to the system ground, to act as a ground drip. the machine in question are Husky Hylectric models.

Thank you, for any and all information.
At an injection plant & large candy company that I worked out the The thermocouple wires were never grounded. Was taught to only ground one end of shield on cables. If you ground both ends the shield might carry current.
 