Re: Thermographic survey
I always call for a thermographic scan if there are shipping splits or bus connections field installed at MCCs, switchboards, etc.
There is always a lot of objection from the Contractor though, since 1) they didn't carry it like they were supposed to and 2) they have to inject rated current, and let things warm up before the scan. And, it always takes three times longer than anticipated, since they inject single phase current, one phase at a time.
Don't forget to require ampere measurements along with the thermal scan. One without the other is often not useful info. And the thermal scanner usually is not the one who will take the amp readings.