A aissuper Member Jul 26, 2004 #1 Is it acceptable to use a thermostat (rated to 22A) to switch a 22A load on a thirty amp CB? Contractor is claiming the contactor must be rated 30A.
Is it acceptable to use a thermostat (rated to 22A) to switch a 22A load on a thirty amp CB? Contractor is claiming the contactor must be rated 30A.
iwire Moderator Staff member Location Massachusetts Jul 26, 2004 #2 Re: Thermostat Contact Ratings Originally posted by aissuper: Is it acceptable to use a thermostat (rated to 22A) to switch a 22A load on a thirty amp CB? Click to expand... If the actual load is 22 amps (before adding 25%) the thermostat would have to be "listed for continuous operation at 100 percent of its rating". 424.3(B) If it is not 100% rated a 22 amp rated thermostat can only be loaded to 18 amps.
Re: Thermostat Contact Ratings Originally posted by aissuper: Is it acceptable to use a thermostat (rated to 22A) to switch a 22A load on a thirty amp CB? Click to expand... If the actual load is 22 amps (before adding 25%) the thermostat would have to be "listed for continuous operation at 100 percent of its rating". 424.3(B) If it is not 100% rated a 22 amp rated thermostat can only be loaded to 18 amps.