At one time if the insulation was rated for, I think, 300vac. But I think they stopped that in 08. Anyway, I can't find it in the book.Can you run the thermostat wires in the same conduit as the power wires?
Then, why is there an issue with running the control wiring in the same raceway as the power conductors with standby generators?300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Then, why is there an issue with running the control wiring in the same raceway as the power conductors with standby generators?
Then, why is there an issue with running the control wiring in the same raceway as the power conductors with standby generators?
Then, why is there an issue with running the control wiring in the same raceway as the power conductors with standby generators?
300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
Then, why is there an issue with running the control wiring in the same raceway as the power conductors with standby generators?
You have to look at the FPN that follows that code section. Most HVAC controls are NEC Class 2 circuits and are covered by the rules in Article 725. Those rules prohibit installing Class 2 control circuit wires in the same raceway as the power circuit wires.300.3(C) Conductors of Different Systems.
(1) 600 Volts, Nominal, or Less. Conductors of ac and dc circuits, rated 600 volts, nominal, or less, shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway. All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.
FPN: See 725.136(A) for Class 2 and Class 3 circuit conductors.
There is an issue, and it is called Article 725.
You have to look at the FPN that follows that code section. Most HVAC controls are NEC Class 2 circuits and are covered by the rules in Article 725. Those rules prohibit installing Class 2 control circuit wires in the same raceway as the power circuit wires.
Class 2 circuit can not be in the same raceway with power circuit but you can reclassify as a class 1 circuit and use chappter 3 as a your wiring methods.
Insulation should be rated for the maximum voltage.
Where it is necessary to locate Class 2 or Class 3 circuits inside the same cable or raceway as
a Class 1 circuit, 725.130(A), Exception No. 2, permits a Class 2 or Class 3 circuit to be
reclassified and installed as Class 1, providing that the Class 2 or Class 3 marking is removed,
that overcurrent protection is provided in accordance with 725.43, and that the reclassified
circuit maintains separation from other Class 2 and Class 3 circuits in accordance with