bpk
Senior Member
- Location
- Northern Minnesota
When you use the thwn rating of a wire can you use the thhn ampacity for dual ratings. For instance I am quoteing a project that has a 225 amp 3 phase disconnect and installing pvc underground to a 225 amp panelboard. The underground wires need to be listed for wet location (right) so they will need to be thwn and 4/0 for 225 amp capacity. If they were thhn 3/0 would work. The reason I would like to know this is because I have some 3/0 copper I would like to use up. Thanks in advance