New to the forums and posting threads. I have an issue I am trying to resolve and hope I can get some help.
I did a little project in a small town where they sub-out the inspections to a private company. On this project, I ran 3/4" sch 40 PVC underground with 4 hots, 4, neutrals, and one ground all #12 THHN. So having between 7 and 9 current carrying conductors in conduit, i calculated the derating as 21a and put on a 20 amp breaker.
The private inspection company failed my inspection saying I had wrong size wire in conduit. He asked me to show him how I arrived at this size wire and after i showed him, he said he didn't believe i was correct and still failed the job.
Can anyone tell me how to prove to him it is correct and/ or what do you do with a private inspection company when they tell you you are wrong, he couldn't prove I was wrong just stated I was wrong, now they won't pay for the job even though they are already using the electric I installed.
I did a little project in a small town where they sub-out the inspections to a private company. On this project, I ran 3/4" sch 40 PVC underground with 4 hots, 4, neutrals, and one ground all #12 THHN. So having between 7 and 9 current carrying conductors in conduit, i calculated the derating as 21a and put on a 20 amp breaker.
The private inspection company failed my inspection saying I had wrong size wire in conduit. He asked me to show him how I arrived at this size wire and after i showed him, he said he didn't believe i was correct and still failed the job.
Can anyone tell me how to prove to him it is correct and/ or what do you do with a private inspection company when they tell you you are wrong, he couldn't prove I was wrong just stated I was wrong, now they won't pay for the job even though they are already using the electric I installed.