D danickstr Senior Member Dec 2, 2007 #1 Is THHN allowed to be pulled underground through SCH 80 PVC and up into bellboxes? Or is THWN required.
Is THHN allowed to be pulled underground through SCH 80 PVC and up into bellboxes? Or is THWN required.
iwire Moderator Staff member Location Massachusetts Dec 2, 2007 #3 You need a conductor with a 'W' in it. XHHW, THW, THWN etc. But I also agree with walkerj that most if not all THHN is dual listed as THWN......most likely THWN-2.
You need a conductor with a 'W' in it. XHHW, THW, THWN etc. But I also agree with walkerj that most if not all THHN is dual listed as THWN......most likely THWN-2.