THHN wire left exposed

Status
Not open for further replies.

Halfcrazy

New member
Ok as an electrician I have always believed THHN wire could not be run in walls etc. Now I am being asked for a code reference stating THHN can not be run inside residential walls without protection. Can anyone point me to the proper place in the 2011 book?
 
Welcome to the forum.:)

Check out 310.10 in the 2011 NEC.

310.10 Uses Permitted. The conductors described in
310.104 shall be permitted for use in any of the wiring
methods covered in Chapter 3 and as specified in their
respective tables or as permitted elsewhere in this Code.

Single conductor THHN installed in a wall is not part of a recognized wiring method covered in Chapter 3.

Chris
 
Ok as an electrician I have always believed THHN wire could not be run in walls etc. Now I am being asked for a code reference stating THHN can not be run inside residential walls without protection. Can anyone point me to the proper place in the 2011 book?

What brought you to this way of thinking??
 
Ok as an electrician I have always believed THHN wire could not be run in walls etc. Now I am being asked for a code reference stating THHN can not be run inside residential walls without protection. Can anyone point me to the proper place in the 2011 book?

What brought you to this way of thinking??

Cavie, did you see the word NOT?
I was brought up thinking the same way. THHN needs to be in conduit.

Is it your thinking that you could run THHN in walls without a raceway?
 
Cavie, did you see the word NOT?
I was brought up thinking the same way. THHN needs to be in conduit.

Is it your thinking that you could run THHN in walls without a raceway?

My BAD. I apologize. I did NOT see the NOT. I read but did NOT see!!!:mad:
 